Здравствуйте все!
На компьютере, где развёрнут SoftLogix установлено:
1) Windows 7 Prof SP1 64 bit Рус.
2) RSLinx 3.51 Запущен драйвер VirtualBackPlane
3) SoftLogix V20.01
4) DEP settings set it to 'Turn on DEP for essential Windows programs and services only'
При первоначальной загрузке программы в SoftLogix загорается красным Battery Fault, что говорит об ошибке "Persistent Storage Fault". Эта ошибка не даёт выгружать программу из SoftLogix и не позваляет стартовать с сохранённой программой.
Как с этим побороться, есть свежие идеи?
Может быть, эти сообраэжения помогут понять причину:
Цитата:
FAQ #1: what causes a RED battery LED on Softlogix5800
It will help to start with a little background. Under the hood,
SoftLogix uses the same software that RSLogix 5000 does to
maintain changes made by another workstation. A heartbeat thread
in RSLogix 5000 periodically asks the controller if any changes
have been logged to the change log. If so, it reads those
changes and applies them to the current image.
Likewise, in SoftLogix, there is a separate process, the
SL5KServer, which has the same thread. The engine communications
with its server via IPC and the server communicates to the engine
using normal communication protocols via RSLinx.
Following download, the SL5KServer opens the image sent to the
engine during download and attempts to go online. Similarly,
following a power cycle (or pull/redrop), the server opens an
ACD, downloads it to the engine, and automatically goes online as
part of a normal download. Either way, once the controller has
an image to run, the SL5KServer should be online.
Every 10 seconds, a thread in the engine asks the server if it is
still online. If it is not, then the engine turns the battery
LED ON (RED) and sends a command to the server to ask it to try
to go online. If the battery LED was not already ON, it also
logs a battery fault. If communications are just busy, the LED
may go RED and then when the comm thread has more time, it may
eventually turn green again. This thread checks every 10 seconds
even if persistent storage save is disabled, since a save will
still occur at powerdown.
Every time interval, the thread referenced above in the engine
will also ask the SL5KServer to perform a save.
Following this, it should be clear that anything that would cause
RSLogix 5000 to go offline will also cause the SL5KServer to go
offline (and hence turn the battery LED RED). A few
possibilities:
Comm thread in engine not responding for 32 seconds.
Any RSLinx communication problem (including a crash).
Loss of communications with the engine.
Loss of correlation.
In addition to these possibilities, the following cases will also
cause a RED LED:
Fatal exception in SL5KServer (including RSLogix 5000
support DLLs).
Any serious error that occurs in the save of the archive:
hard disk errors, insufficient disk space, etc.
Проблема была в том, что RSLogix5000 у нас был версии 20.03. Ключевое здесь - это .03. Как нам объяснили в Rockwell (Москва) версии пакетов с таким индексом особо защищены и корректно работают, только со своими версиями контроллеров. У нас стоял SoftLogix 20.01.
Взяли RSLogix5000 20.00 и всё правильно заработало
Вы не можете начинать темы Вы не можете отвечать на сообщения Вы не можете редактировать свои сообщения Вы не можете удалять свои сообщения Вы не можете голосовать в опросах
Smart Solutions VDT GmbH | Friedrich-List-Allee 38, D-41844 Wegberg-Wildenrath, Germany Tel.: +49 2432 933 57 83 | e-Mail: office@vdt-solutions.de Все товарные знаки и торговые марки являются собственностью их владельцев.
При использовании материалов сайта ссылка на данный сайт обязательна. Открытие страницы: 0.131 секунды