При экспорте базы тегов RSViewSE 4.0 получается ошибка Problem Launching 'TagSVRTC' - 'TagDBImpExp'
Tag Import/Export Wizard require the VStudio application to be open.
В базе знаний ответы в основном с уровнем доступа TechConnect. Помогите разобраться, очень нужно сделать экспорт тегов. А может есть для SE утилита типа Project Documentation RSView32?
Cause:
The following have been identified as causes for this error:
* the HMI server is located on a remote machine - attempting to import/export tags to a remote HMI server is not supported;
* the local HMI server is not running - for the Tag ImpExp utility to function correctly the tag server (TagSrv.exe) must be running;
* the default web page for the computer is not running;
* the tag cache files for the HMI server have become corrupt;
* if running RSView SE version 3.00.01 see AID 26896 - Problem Launching 'TagSVRTC' - 'TagDBImpExp' after applying Patch from R59554218
* if running RSView SE version 4.00.00 (CPR 7), the logged in user to FactoryTalk is not part of this project's RSView User Accounts; and
* a remote Terminal Services session is being used to import a CSV file on a Windows 2000 Server computer hosting the HMI Server.
* importing to a primary and secondary HMI server, simply stopping the HMI server service as a failover in order to update the 'other' server will generate this error. Disconnecting the ethernet cable from the PC is a more effective failover and will allow for the import/export to work.
Solution:
To turn on the default web page:
1. Go to Control Panel-> Administrative Tools.
2. For Windows 2000, launch "Internet Services Manager".
3. For Windows XP, launch "Internet Information Services".
4. Drill down the folders until underneath this computer name you see "Default Web Site". If it has the word "Stopped" next to it, right-click it and choose "Start".
To Resynchronize the HMI server's tag database by deleting the tag cache files:
1. Find the HMI Server folder for the problem tag database in Windows Explorer (i.e., C:\Documents and Settings\All Users\Documents\RSView Enterprise\SE\HMI Projects\<HMIServerName>).
2. Delete the 'cache' subfolder and also the CAC file in the 'Tag' subfolder (i.e., <HMIServerName.CAC).
3. Reboot the machine to force a re-resynchronization of the tag database.
Note: the tag database is re-synchronized when the HMI server starts. If the HMI server is configured to start on system startup (on reboot), it is not necessary to open and load the application in View Studio. If the HMI server is configured to start on demand, the server will only start once a client (either View Studio or Display Client) is run.
If Windows 2000 Server (as an HMI Server) is setup for use with Terminal Services, use the local console instead of a remote Terminal Services session for the Import.
If using RSView Studio 4.00.00 (CPR 7), the logged in user to FactoryTalk must be an authenticated user to the application. Please do the following:
1. Launch RSView Studio and open your application
2. Go to Settings and select RSView User Accounts
3. Click on the icon labeled Add User/Group
4. Click on Add and select the desired FactoryTalk User and hit OK
5. Check Allow "All Actions" for the user that was just added and hit OK
6. Click "Close" on the right to exit out of the User Accounts window and click Yes to Save changes to document
Вы не можете начинать темы Вы не можете отвечать на сообщения Вы не можете редактировать свои сообщения Вы не можете удалять свои сообщения Вы не можете голосовать в опросах
Smart Solutions VDT GmbH | Friedrich-List-Allee 38, D-41844 Wegberg-Wildenrath, Germany Tel.: +49 2432 933 57 83 | e-Mail: office@vdt-solutions.de Все товарные знаки и торговые марки являются собственностью их владельцев.
При использовании материалов сайта ссылка на данный сайт обязательна. Открытие страницы: 0.127 секунды